  • What is the optimum level of excess air in a natural draft heater?

    Apr-2021

Answers


  • Jake Gotham, InSite Technical Services, jake.gotham@insitetechnical.com

    Previous answers have given various rules of thumb which are useful for design purposes or for initial screening to identify the most likely opportunities for improvements.  In a multi-burner natural draught furnace, it is very difficult to reliably set all the registers to give equal air to each burner, hence a certain amount of sub-optimisation is almost inevitable.

    To get maximum benefits from optimisation, and to ensure optimisation doesn’t create safety or environmental issues, the oxygen analyser should be coupled with a combustibles analyser.  Ideally the analysers should measure conditions below the convection section due to the large amount of air leakage in a typical convection section.

    The objective is to simultaneously minimise excess oxygen and combustibles.  One approach is to reduce air until the combustibles respond, then reverse the last movement on the air.  Another is to multiply the %O2 by the combustibles measurement, and minimise the product by adjusting the air.

    A skilled, experienced, committed operator is more important than the optimisation method, analyser type or control technology.  Edwin mentioned above the issue with operator priorities affecting their ability to commit time to continuous optimisation. I know of several sites that have tried to address this by creating an additional operator position dedicated to furnace tuning. This individual spends his shift moving from furnace to furnace optimising the firing conditions – obviously in close communication with the unit operator.  It is not difficult for this individual to cover the cost of his employment.

    Apr-2021

  • Grant Jacobson, Becht, gjacobson@becht.com

    It depends on the heater design and operating objectives. For most applications, optimised excess air (or excess oxygen if discussing on just an O2 basis) can be set between 15% and 25%. To confirm where this can be optimised safely it is important to conduct a CO breakthrough test and then set the optimisation targets based on where CO breakthrough is observed. An example of this would be if CO breakthrough occurs at 1.5% excess O2; the target to operate normally would be set at 3.0-4.0% excess O2. It is critical to not lose sight of keeping fired equipment stable and safe, and optimising to reasonable targets when able to do so.

    Apr-2021

  • Edwin Voeten, Petrogenium, Edwin.voeten@petrogenium.com

    Optimal value excess air should be evaluated on a case-by-case basis. However, as a design case 3 vol% O2 in flue gas is typically used, which corresponds to some 15% excess air over the stoichiometric requirement.

    The use of a forced draft fan is done for technical, economic, and/or historical reasons.

    The incentive to lower excess air is economics. As a guideline, some 1% fuel efficiency can be gained for every 2 vol% of O2 reduction in flue gas. Excess air is easier to control by use of a forced draft fan (together with other benefits from a forced draft arrangement). However, this requires additional capex. Consequentially, a forced draft arrangement is typically used in larger heaters.

    In a natural draft heater, for every process change or upset an operator may need to make changes to individual burner air registers in the field (and draft control/stack damper as well). Significantly, there may be an incentive to move towards forced draft where operation is expected to be less stable. Alternatively, in a natural draft unit a wider margin in excess air (a higher value than the design value) can be used to minimise the risk of sub-stoichiometric firing from any operational changes or upsets. This then has an economic penalty (see the numbers above).

    As a result, it is not uncommon to see a natural draft unit in the field operate in the 4-5 vol% O2 range, or higher. Although I should mention that this often is a consequence of operational staff having ‘other priorities’ and improvements are feasible.

    Note that this refers to gas fired natural draft units, which is the standard. I know of less than a handful of oil fired natural draft units (in Turkey, Kazakhstan, and Russia). Such units should not have been designed with the combination of fuel oil and natural draft, as this is a continuous source of trouble. Last thing I heard, the unit in Turkey was to be converted to forced draft.

    Apr-2021

  • John Skelland, KBC (A Yokogawa Company), John.Skelland@KBC.global

    Aim to operate the heater at its original design excess air level in the first instance. A good performance in modern heaters is 10% excess air (2% oxygen in the flue gas) for heaters fired with fuel gas. Fuel oil fired heaters usually require 15% excess air (about 3% stack oxygen). This is often due to fuel oil burners being slightly more difficult to tune and operate. Operating at these low levels is made easier if automatic control is installed rather than relying on frequent attention from the operators.

    It is sometimes possible to safely operate fired heaters at stack oxygen contents as low as 1% (~6% excess air) if an advanced control system such as Yokogawa’s Combustion One is installed. This system, incorporating tunable diode laser spectroscopy (TDLS), gives fully automatic control and optimisation of the combustion process. It measures oxygen, carbon monoxide, and methane concentrations in the flue gas to prevent the risk of unstable combustion.

    Apr-2021



  • Responsive image Ball valves for pipelines and refineries
  • Responsive image Processing heavy canadian crude
  • Responsive image Be future forward
  • Responsive image Axens on Youtube
  • Responsive image Process burners
  • Responsive image SSX™ Technology
  • Responsive image Oil and gas water treatment applications
  • Responsive image Jet mixers for tank mixing and blending
  • Responsive image FCC catalysts & additives
  • Responsive image Distillation Experts Conclave
  • Responsive image FluegasExact 2700 effective combustion analysis